edison123: The magnetics of the motor are designed for a maximum flux density - which can be directly correlated to volt/hertz. If you juggle parameters to increase the slope (more volts for same hertz, or less hertz for same volts) you WILL have a problem. Other than the built-in "voltage boost" function on most modern drives, there is no good way to accomplish the slope change while the machine is moving - if you want it operate correctly afterward. Most drives also have either a "timer" or a "comparator" function tied to the voltage boost profile so that the switchover to the regular ramp occurs when there will be minimum disturbance in the run-up.
The drive should be capable of providing the no-load loss for the machine (friction, windage, copper loss, iron loss) - which should be fairly low for an MV machine rated for the power rating you envision. Then add a bit more, because somewhere down the road you will likely want to expand your capabilities to include a larger test article. Also recall that your acceleration time is a result of torque applied against system inertia. If you keep the current low, it will take forever to accelerate. The trade-off is that higher (than nameplate) currents create extra heat, which ultimately shortens the life of the windings and other components. No issue if the current limit is set below nameplate, though.
Converting energy to motion for more than half a century