EngPhenomena
Civil/Environmental
There is an existing inlet on an aircraft fueling ramp that is in question. The proposed project calls for extending the building to provide additional gates. The inlet happens to be in the main stormwater trunk line and it will now be underneath the proposed building extension.
NFPA 415 has language about drainage inlets being set back a minimum of 50 feet. We plan on changing it to a manhole. The grades also need to meet NFPA requirements which call for minimum 1 percent grade away from all airside structures for the first 50 feet.
The manhole will end up being a high point. The confusion is this paragraph.
5.1.4 "The drainage system of any aircraft fueling ramp shall be so designed that the fuel or its vapor cannot enter into the drainage system of buildings, areas utilized for automobile parking, public or private streets, or the publice side of airport terminal or aircraft hangar structures...."
My interpretation is that as long as the stormwater system is independent of the above statement it would meet code.
Knowing that fuel and vapor can still get into the stormwater system the following options are being evaluated:
1. Move the manhole structure outside the set back. Very expensive.
2. Can a junction structure be installed without access. Least Expensive.
NFPA 415 has language about drainage inlets being set back a minimum of 50 feet. We plan on changing it to a manhole. The grades also need to meet NFPA requirements which call for minimum 1 percent grade away from all airside structures for the first 50 feet.
The manhole will end up being a high point. The confusion is this paragraph.
5.1.4 "The drainage system of any aircraft fueling ramp shall be so designed that the fuel or its vapor cannot enter into the drainage system of buildings, areas utilized for automobile parking, public or private streets, or the publice side of airport terminal or aircraft hangar structures...."
My interpretation is that as long as the stormwater system is independent of the above statement it would meet code.
Knowing that fuel and vapor can still get into the stormwater system the following options are being evaluated:
1. Move the manhole structure outside the set back. Very expensive.
2. Can a junction structure be installed without access. Least Expensive.