Hi All
We have a site where the existing 7.6 kV/ 433V 200kVA transformer is being replaced with a 750kVA transformer. I am told by the site electricians that the phase rotation of the existing system is 'not right' (they can't tell me any more detail than that)
Now, we are replacing the TF with a new unit and we have to make sure that the phase rotation of the new installation results in the same motor turning direction as the old rotation.
I have thought about this a bit and I think I have it straight but I am an engineer, not a technician, I have never measured phase rotation etc so I fear I am missing the more practical part of the issue.
This is what I was thinking:
1)Measure existing site phase rotation using rotation meter that will tell us if the rotation is CW or CCW.
CW denotes R, W, B, R, W, B....
CCW denotes R, B, W, R, B, W...
2)The new transformer has the intended phase rotation direction marked on the nameplate, it shows:
R, B, W, R, B, W...
So essentially if our phase rotation test comes out to CW, we have to swap the B and W phase (for example) between the LV side of the TF and the MCC. If the existing phase rotation is CCW, we simply connect R, W, B to R, W, B
Haha I am explaining this in an elementary way, only because I am trying to account for every eventualuty that may occur on site when this is done
Would appreciate any info. Thanks.
We have a site where the existing 7.6 kV/ 433V 200kVA transformer is being replaced with a 750kVA transformer. I am told by the site electricians that the phase rotation of the existing system is 'not right' (they can't tell me any more detail than that)
Now, we are replacing the TF with a new unit and we have to make sure that the phase rotation of the new installation results in the same motor turning direction as the old rotation.
I have thought about this a bit and I think I have it straight but I am an engineer, not a technician, I have never measured phase rotation etc so I fear I am missing the more practical part of the issue.
This is what I was thinking:
1)Measure existing site phase rotation using rotation meter that will tell us if the rotation is CW or CCW.
CW denotes R, W, B, R, W, B....
CCW denotes R, B, W, R, B, W...
2)The new transformer has the intended phase rotation direction marked on the nameplate, it shows:
R, B, W, R, B, W...
So essentially if our phase rotation test comes out to CW, we have to swap the B and W phase (for example) between the LV side of the TF and the MCC. If the existing phase rotation is CCW, we simply connect R, W, B to R, W, B
Haha I am explaining this in an elementary way, only because I am trying to account for every eventualuty that may occur on site when this is done
Would appreciate any info. Thanks.