One thing we have done, which some may think is "scary" on old joists when you don't know exactly what you have, is to re-do the original design, doing a dead load takeoff of the floor or roof, and then apply the live load (or snow load) that was applicable at the time of the original design. In our area, years ago most engineers used 30 psf for snow. Today, with the IBC, the snow is around 21 psf so we have some extra capacity to play with.
You can build an original shear and moment diagram capacity envelope based on these assumed original design loads and then compare with your current loading condition to see where you are at. The BIG assumption in doing this is that you assume that the original engineer correctly designed the dang things.