The only IEEE standard that comes to mind is IEEE 690 which gives criteria for a DC-voltage insulation resistance test for cables <600 volts. The failure mechanism for LV cable <600 voltage is completely different than the failure mechanisms of MV or HV cables. IEEE 400 recommendations against the use of DC for MV and HV cable should not be extrapolated to testing LV cables.
Since LV cables are not shielded, a withstand test is next to useless because the voltage stress distribution across the cable insulation is not equal along the length of the cable. However, if there is a ground plan near a part of cable insulation, that part will be stressed. If there happens to be a crack in the insulation being stressed, some leakage may be recorded by a sensitive micro ammeter. Go ahead and megger, hipot, all you want, but understand the risk that you can have a failure literally one minute after reenergization with out warning. One minute should be more than sufficient to detect leakage current issues.
Benjamin Lanz
Vice Chair of IEEE 400
Sr. Application Engineer
IMCORP- Power Cable Reliability Consultants