This is part process cooling and most HVAC.
I run 39F in summer because it dehumidifies a lot.
I need a dew point of 44F in the end of the dehumidification coils.
We are talking about 850,000 of make up air, (100% OSA units).
The dehumidification coils were designed for 40F. In the rest of the year I reset the SP, it can go up to 42.5F.
Tertiary pumps are in part of this system, 6,500,000 CFM on recirculation units, doing 2F delta T (air side) but most of the load is on the secondary system. There are NO 2 way control valves at the individual buildings to hold back the return water until the it warms to 55-56F.
There are no 3 way valves, each coil has its control valve (proportional Baumann butterflies).
I have no real balancing valves on the condenser water and chiller water pipe before the chillers. We managed to balance it with 18" butterfly valves before each chiller, which was a nightmare.
There are actually hundreds of coils on this system. I have to check the coil arrangements.
In fact I am dying to change this to variable primary flow, but have no way to justify this financially yet...