Switchgear heaters. Switchgear may have thermostatically controlled heaters to avoid operating problems in cold climates.
These heaters are used to keep the temperature of the mechanism above the point where mis-operation may occur.
Cold weather heaters are a greater capacity than anti-condensation heaters.
I have seen switchgear with both thermostatically controlled heaters, and 24/7 connected anti-condensation heaters.
The issue with motors and generators and condensation is thermal lag.
In conditions of rising temperatures and dew points, the thermal lag of the core iron may lag behind the dew point even though the ambient temperature is above the dew point.
The motor manufacturer should be sizing the heater to bring the entire motor frame (including the windings) to roughly 5 C above the dew point. That means they have to know where the machine is going to be installed, so they can estimate the dew point.
I find that statement a little misleading on two points;
The dew point is dependent on both the ambient temperature and on the relative humidity. Estimating a widely variable effect may not be particularly valuable.
The heat added by the anti-condensation heater keeps the core above the ambient temperature. When the ambient temperature rises without the addition of moisture, the relative humidity drops.
The dew point rises when moisture is added to the local atmosphere.
The purpose of the anti-condensation heater is to combat the thermal lag of the core and keep the core temperature above the dew point when both the ambient temperature and the dew point are rising.
An example may help:
My greatest concern for condensation in our generators was a combination of a chilly night followed by a rapidly rising ambient temperature on a cloud free tropical morning, and a strong, moisture laden on-shore breeze.
--------------------