engrom
Materials
- Jul 31, 2003
- 92
Friends,
We've a scenario in one of our gas plants: A106B 14" piping sch 80, WT 0.75" (no PWHT) is installed for design pressure 15MPa. Normal operating 3.5MPa, max pressure the system will see is 10MPa. As per curve B, the min temp it can go is -10degC without impact test. In winter months, the pipe can see temp below -15degC becoz of some J-T effect across the throttling valve. Is this permissible to operate below -10deg without impact test. Can we apply temp reduction factor in Fig 323.2.2B?
We've a scenario in one of our gas plants: A106B 14" piping sch 80, WT 0.75" (no PWHT) is installed for design pressure 15MPa. Normal operating 3.5MPa, max pressure the system will see is 10MPa. As per curve B, the min temp it can go is -10degC without impact test. In winter months, the pipe can see temp below -15degC becoz of some J-T effect across the throttling valve. Is this permissible to operate below -10deg without impact test. Can we apply temp reduction factor in Fig 323.2.2B?