tctctraining
Electrical
- Nov 17, 2008
- 118
Hydro defines low inst. setting on their breaker to protect temp. faults on the line.
If we add a new recloser , we can't trip faster than the breaker and trip before breaker unless a time delay is introduced on breaker low inst. setting or raise the low inst.
the issue is that there is another feeder off the TS which doesn't have any recloser and using time delay on low set will delay temp faults on that line and that will probably damage the line.
low set is set for line current value which is lamost 600A.
I woould be interested in discussing this with exerts out there and appreciate your feedbacks.
Thanks