"Loop impedance" is an IEC thing that has no place in the NEC realm. IEC stuff and IEC requirements work well in an IEC environment while ANSI (including NEC) stuff and ANSI requirements work well in an ANSI environment. But never the twain shall meet. You have to pick one and take the whole package; you can not build a complete package by taking bits and pieces from one and different pieces from the other and trying to make a hybrid. Won't work.
The "problem" is that there are a variety of underlying, but often not explicitly stated, assumptions upon which the practices are built. For instance, for single family residential installations, in the NEC world the service transformer will have a 240V single phase low-side with a solidly grounded mid-point tap. This produces services with two phase conductors, 240V between, and 120V between each and the neutral from the tap. A large service transformer will serve as many as 10 houses, each on its own radial connection.
On the other hand, as I understand it, in the IEC world the service transformers are considerably larger, are not solidly grounded and supply 3-phase services to many 10s of houses, on loops rather than radially, and cover considerably larger areas.
Other than the fundamental physics involved nothing is the same, nothing is compatible. They each work, but no portions of either are compatible with the other.
I’ll see your silver lining and raise you two black clouds. - Protection Operations