rockman7892
I have a 4.16kV 250 hp motor that has been tripping recently and I cannot seem to figure out why. The FLA for this motor is 29A and the LRC value on the motor datasheet is 192A. After the motor tripped last I went to the multlin 269 protecting this motor and noticed that the motor was tripping at a value of 190A. Does this mean that for some reason the motor is approaching or seeing its LRC? Would this mean that something is jamming or stopping this motor and locking up the rotor? Can a motor ever draw more current than its LRC?
The application this motor is being used for is a fan which is pulling draft through a mill. The draft is controlled by a damper which is upstream of the fan.
If I understand correctly LRC is the current necessary to overcome a rotor from the standstill or locked/stalled position. It is a direct result of the torque required to overcome the inertia of the rotor. Any ideas on why this motor would be tripping at this value?