I have seen several threads that agree that you should avoid designing CMU elevator core walls assuming you get coupling action from the lintel, since it is difficult to get the loads to work. This follows guidance from NEHRP Seismic Design Technical Brief No. 9, where testing showed that even when adding a control joint on both sides of an opening, coupling action in the lintel was still observed.
I am modeling an elevator core as a C shape w/ lips, but am having trouble understanding where to put a wall control joint and how to verify the lintel will be ok and protected against coupling forces. Since this is an exterior elevator core that is being located adjacent to an existing building, the walls are spanning horizontally and I need the returns/lips of the C shape to provide support for out of plane forces; this is why I do not want to add a CJ on each side of the opening.
The control joint is only being provided to break up the shear walls. Since I have so much horiz reinf., my crack control req'mts should be met without adding CJ's.
How have you handled this situation in the past? See attached for hand sketch of scenario.
Thanks.
Thanks.