All,
I work for a rural distribution cooperative and am playing with some station loss contingency scenarios in a commercially available model. I am running into what I believe to be a limitation of the model itself, but would like some opinions.
I have a scenario where I must serve a substation from a neighboring substation 10 miles away. The distance of the feeder and size of the load is bringing my voltage down to 80-90V. I think this is because I am modelling the loads as constant power. If the voltage goes down, the current must go up, increasing losses, further bringing my voltage down, and so on, in order to maintain my demand.
What would really happen in this scenario? Resistive loads would not force more current to flow. Motors maintain a constant power for a certain voltage range... but would a motor maintain constant power if a 0.7pu voltage was applied to it, for example?
I have a station that serves 4MW of load... under this contingency I get 80V, 4MW of load, and 2MW of loss. I wonder if anyone has seen this and can explain what really happens.
Thank you
I work for a rural distribution cooperative and am playing with some station loss contingency scenarios in a commercially available model. I am running into what I believe to be a limitation of the model itself, but would like some opinions.
I have a scenario where I must serve a substation from a neighboring substation 10 miles away. The distance of the feeder and size of the load is bringing my voltage down to 80-90V. I think this is because I am modelling the loads as constant power. If the voltage goes down, the current must go up, increasing losses, further bringing my voltage down, and so on, in order to maintain my demand.
What would really happen in this scenario? Resistive loads would not force more current to flow. Motors maintain a constant power for a certain voltage range... but would a motor maintain constant power if a 0.7pu voltage was applied to it, for example?
I have a station that serves 4MW of load... under this contingency I get 80V, 4MW of load, and 2MW of loss. I wonder if anyone has seen this and can explain what really happens.
Thank you