- Nov 21, 2006
- 38
Anybody know the definition of LOAD DIVERSITY for adjusting the ampacity of conductors in a raceway? Table B.310.11 allows increasing the ampacity of conductors in a raceway, but I can't find a basis for determining what is 50% load diversity.
I need 18- 10ga. conductors to feed a batch of 1KW lights. Using table 310.11, I can only put 9 conductors in a raceway, or the ampacity is reduced from 70% to 50%. Table B.310.11 allows 70% multiplier for 10-24 conductors if load diversity is allowed.
As these are known fixed continuous loads, and all but ground wires will be handling the load, I believe I have to use the 9 conductor limit, just looking for confirmation.