It's a great piece of legislation isn't it!
EAW 1989 Reg 14 said:
No person shall be engaged in any work activity on or so near any live conductor (other than one suitably covered with insulating material so as to prevent danger) that danger may arise unless–
(a)it is unreasonable in all the circumstances for it to be dead; and
(b)it is reasonable in all the circumstances for him to be at work on or near it while it is live; and
(c)suitable precautions (including where necessary the provision of suitable protective equipment) are taken to prevent injury.
You need to be able to demonstrate, possibly in court if things turn to crap, that:
- there are good reasons why the work has to be performed live, for example isolating the equipment to allow dead working might introduce a geater risk elsewhere.
- methods exist which allow the work to be undertaken in a safe manner
- the risks associated with performing the work live can be adequately managed and reduced to an acceptable level
In common with much of the UK's safety legislation, the judgement of what is or isn't an acceptable level of risk in your specific circumstances is yours to make. That's unless something goes wrong, then the judgement gets made by someone else, in court, based on evidence from the HSE. One of the most important questions to ask yourself is 'Could I explain my decisions or my actions to a jury?', and if you find that you can't answer that question comfortably then perhaps you need to re-evaluate what you're doing or what you're considering doing.
----------------------------------