Irishal:
A -40
oC design temperature is appropriate for your liquid CO
2 storage tank if the design steel is rated and approved for that working temperature in accordance with the stress required.
You should have all the documentation for your tank and studying it you should be able to find the applicable design calculations and/or specifications. I’m in the USA and have always built my vessels in accordance with ASME Section VIII, so I’m not familiar with European or UK codes. I do know that the steel I use for liquid CO
2 tanks is only good down to -20
oF (-28.9
oC). I suspect that this is also the case in the UK.
I kind of suspect that the steel grades in both the USA and the UK follow each other very closely in acceptable stress and temperature values and that you will not be able to get to a -40
oC design without going into special low temperature steel grades.
The chart you request for saturated liquid CO
2 can be found at the following webpage within the NIST (National Institute of Standards and Technology) website:
Note that the NIST data tells you the corresponding
absolute pressure for your tank at the corresponding temperature. If your tank is designed for an operating pressure of 20 barg, then the corresponding design temperature is approximately -18
oC --- which is far different from what you are seeking (-40
oC). Liquid CO
2 as stored by you is in the saturated state and the pressure and temperature are related to each other as shown in the NIST table I refer you to. That means that if you intend to operate the tank at 20 barg, then for all practical reasons you have fixed the operating temperature at -18
oC ---which not too coincindentally comes out to be almost the same as to what we do here in the USA.
I hope this information helps out. I took the liberty of selecting what I thought would be your preferred SI units for the Thermodynamic values given in the NIST webpage. You can always change these to other units if you so desire by simply going to the NIST homepage. Also note that although this may not be of any interest to you, the NIST Thermo data does not go into the solid (Dry Ice) CO
2 phase. If you later want this data you must go elsewhere to obtain it for now.