- Aug 5, 2008
- 3
I am sizing lintols for a friend who is planning a house extension.
He wants to create a wide opening in the existing rear elevation. The width of masonry remaining either side of opening will be 600mm one end but only 300mm other end (basically thickness of cavity gable wall perpendicular to rear elevation).
BS 5977-1 'Lintels - Method for assessment of load' Clause 5e requires masonry either side to be 600mm or 0.2 x clear span, whichever is greater.
Do I just have to design lintol to carry FULL vertical loading rather than load triangle and any loads in interaction zone ie. no arching action? What checks do I need to make regarding strength and stability of remaining narrow brick pier?
Many thanks for any advice offered.
He wants to create a wide opening in the existing rear elevation. The width of masonry remaining either side of opening will be 600mm one end but only 300mm other end (basically thickness of cavity gable wall perpendicular to rear elevation).
BS 5977-1 'Lintels - Method for assessment of load' Clause 5e requires masonry either side to be 600mm or 0.2 x clear span, whichever is greater.
Do I just have to design lintol to carry FULL vertical loading rather than load triangle and any loads in interaction zone ie. no arching action? What checks do I need to make regarding strength and stability of remaining narrow brick pier?
Many thanks for any advice offered.