You have several pushbuttons. If the system shuts down how do you know which button it was?
If you use a button with 1 NC and 1 NO you can wire the NO contact back to the control panel and read it with an analog input or simple Voltmeter
One way I have seen on a 2 kilometer conveyor was to have a series resistor at each switch feeding one side of the NO switch with 1V, 2V, 3V, 4V etc when a switch was pulled by the Voltage feeding back the operator knew which switch was pulled, if 2 switches were pulled it would display the closest one first. A 4 core cable was used daisy chaining from switch to switch.
Of course if all your switches are close you can wire them all back to a common location and monitor them with a PLC inputs, whatever you do don't compromise the ability of the switches to interrupt the power to the safety shutoff device.