There are formulas for calculating positive and zero sequence impedances, however if you don't know the values (positive sequence impedance is provided by the manufacturer and does not change zero sequence depends on soil quality, season etc), the best thing to do is to carry out a Line Parameter Testing. To do that, you need to de-energise the line and carry out injections to the next substation. If there is another line on the same tower, you will need the zero sequence mutual impedance between the two lines as well, because in case of one line out of service and earthed at both ends, your zero sequece impedance can change considerably.
If injection is not possible find what type of conductors are used and refer to manufacturer information. For overhead lines the angle is around 75 Deg. If you can not find any information on conductors, use 0.4 ohm/km as a safe approximation.