Histor (Electrical)(OP)23 Aug 24 05:14
'There are highest structure which are 6m tanks, 9m street light poles are nearby. But I don't see any lightning protection for them...Since there are no lightning for those structure it can not fully protect my shelter. Is my opinion makes sense?'
1. I am convinced that you are very prudent, have very good experience/knowledge and have done your research thoroughly on the matter raised.
1.1 BTW: Are you facing difficulties with the insurance Co. or inspector ? You may have to out source it to UL for their expert service.
2. Those nearby high structure 6m tanks (if metallic), 9m street metallic light poles if they are Earthed to say <5 Ohm, would act as strike terminals, irrespective whether any visible lightning protection installed with them.
3. Based on 2. above, I am of the opinion that the 3m shelter is Fully lightning protected. Also 3m + 1m terminal need NO "Wind load calculation".
4. Attention: The shelter conductive surfaces, MCC and any extraneous conductive surfaces MUST be BONDED and EARTHED to say <5 Ohm. Note: It is usual for lightning protection, the earthing resistance is higher, say <10 Ohm.
Che Kuan Yau (Singapore)