LH Joist minimum shear stength 1

Status
Not open for further replies.

TedEP

Structural
Feb 3, 2011
15
I have seen references stating the minimum shear strength of a K-series joist is 25% of the end reaction.

Where is this stated in SJI specs?

Is it the same for LH series?

Thanks for the help
 
Replies continue below

Recommended for you

The minimum web shear strength requirement is in section 4.4.2 of SJI 100-2015 (Standard Specification for K-Series, LH-Series, and DLH-Series Open Web Steel Joists and Joist Girders, effective January 1, 2015). So, yes, the requirement is applicable to LH-Series joists as well. The requirement is in section 4.4 of the 2010 K-Series standard specification and section 103.4 of the 2010 LH- and DLH-Series standard specification.
 