Unfortunately it is not possible to apply any significant voltage/amperage to the generator. This is due to the fact that it is designed to run inside a can, submerged at very low temperatures. To get access to the 6 leads the machine must be drained and warmed-up. In this state any significant current will potentially damage the machine. Additionally this is being done a site that has rules that severely limit higher voltages.
It has been decided that the machine will be pulled out completely and taken to a workshop. One idea that came-up was using a phase rotation meter. The question with this is would it only confirm the the correct order of phases in each wye or can it also confirm the correct pairing between the wyes (a1-a2, etc)?
For reference, we tried the following test on a spare generator of the same design, but with known correct phase marking. I have been told that the orientation of the wyes are such that one wye is rotated 60degrees from the other. Essentially if you imagine a typed "Y", you have one upright and one inverted.
Apply a small voltage/amps to wye1 as indicated. Measure induced voltage on wye2.
Apply 25VAC/1.8amps to Wye1 a1-b1, induced voltage results: a2-b2=3.36V,b2-c2=1.71V,c2-a2=1.66V.
Apply 25VAC/2.4amps to Wye1 b1-c1, induced voltage results: a2-b2=2.00V,b2-c2=10.80V,c2-a2=8.80V.
Apply 25VAC/2.4amps to Wye1 c1-a1, induced voltage results: a2-b2=2.10V,b2-c2=8.75V,c2-a2=10.89V.
Then apply power on wye2 and measure on wye 1:
Apply 25VAC/1.8amps to Wye2 a2-b2, induced voltage results: a1-b1=3.36V,b1-c1=1.50V,c1-a1=1.70V.
Apply 25VAC/2.3amps to Wye2 b2-c2, induced voltage results: a1-b1=2.10V,b1-c1=10.90V,c1-a1=8.80V.
Apply 25VAC/2.3amps to Wye2 c2-a2, induced voltage results: a1-b1=2.10V,b1-c1=8.80V,c1-a1=10.90V.
The results were not quite what was predicted. It was thought that for each wye1 phase energized, there would be one wye2 phase voltage that would be 1.5-2 times higher than the others. Any ideas on why the results did not come out as expected? I do not know why the first phase powered, used less amperage as I was not present at the actual testing. I would imagine voltage magnitudes would be different, but the relation between the three wye2 phase voltages should be consistent.
Any help would be appreciated, especially regarding the use of the phase rotation meter.