I am looking for a double check on my reasoning in applying the provisions of the International Residential Building Code. The section in particular is 602.10.1 of the 2000 IRC.
This section requires wall sections that are less than 2'8" long to be braced by special design as the code does not address this point. This comes into play for the little wing walls on either side of a garage opening. I have been working in both the commercial and residential areas of structural engineering for quite some time. I must agree with the code that these wing walls must be braced properly, but I have found myself in disagreement with 'other' engineers in my area.
As one would analyze a lateral load resisting wall as a shear wall, I am analyzing the opening of the garage as a portal frame that must resist induced moments from wind loading on the side wall. My analysis is very similiar to how one would analyze a moment resisting builiding bent for a commercial structure.
In this lies my issue: I am factoring the moment resistance all the way down to the footing and I am coming up with larger than average footing sizes and that the reinforcement must extend into the footing. This not unlike the analysis and detailing one would expect to find on a set of commercial building plans. Most of the 'other' engineers in my area are not carrying the reinforcement down to the footing, merely to the masonry foundation wall below with J-bolts...but unreinforced masonry cannot resist axial tension. Alot of my clients have voiced concerned over the difficulty in constructing this type of braced frame system but they do agree with my thinking. Unfortunately several people want to use the 'other' engineer's methods because they are easier to construct. I would like to reference any respondants to this thread to the Simpson Strong Tie 'Strong Wall'...basically this is the same thing that I am doing, but like Simpson I am connecting the wall through the masonry foundation wall to the footing.
The way I look at it, if the code doesn't cover it, one must exercise sound engineering judgement in the analysis. My judgement is to not cut corners and do what I feel is right, but the local building jurisdictions in NC are accepting the, in my opinion, lackluster designs of others. Any other interpretations on this codes section? Esecially from those working in Hurricance country. I have the ethical issue well in hand, but I am starting to think about the client retention issue.
To elaborate: The typical garage opeing is 10' tall by 18' wide and assume that the header is the top of the bent. The wing walls are 2' wide braced panels that rest on a 8" wide unreinforced masonry wall of the same length, these are the side verticals of the bent. The lateral force applied to the top corner of the bent is around 10,000#. The way I calculate it, the moment at the bottom of the braced panel must be transmitted to the footing, through the foundation wall with reinforcing bars, not just J-bolts in the masonry alone.
Thanks for any help or insight you may offer.
This section requires wall sections that are less than 2'8" long to be braced by special design as the code does not address this point. This comes into play for the little wing walls on either side of a garage opening. I have been working in both the commercial and residential areas of structural engineering for quite some time. I must agree with the code that these wing walls must be braced properly, but I have found myself in disagreement with 'other' engineers in my area.
As one would analyze a lateral load resisting wall as a shear wall, I am analyzing the opening of the garage as a portal frame that must resist induced moments from wind loading on the side wall. My analysis is very similiar to how one would analyze a moment resisting builiding bent for a commercial structure.
In this lies my issue: I am factoring the moment resistance all the way down to the footing and I am coming up with larger than average footing sizes and that the reinforcement must extend into the footing. This not unlike the analysis and detailing one would expect to find on a set of commercial building plans. Most of the 'other' engineers in my area are not carrying the reinforcement down to the footing, merely to the masonry foundation wall below with J-bolts...but unreinforced masonry cannot resist axial tension. Alot of my clients have voiced concerned over the difficulty in constructing this type of braced frame system but they do agree with my thinking. Unfortunately several people want to use the 'other' engineer's methods because they are easier to construct. I would like to reference any respondants to this thread to the Simpson Strong Tie 'Strong Wall'...basically this is the same thing that I am doing, but like Simpson I am connecting the wall through the masonry foundation wall to the footing.
The way I look at it, if the code doesn't cover it, one must exercise sound engineering judgement in the analysis. My judgement is to not cut corners and do what I feel is right, but the local building jurisdictions in NC are accepting the, in my opinion, lackluster designs of others. Any other interpretations on this codes section? Esecially from those working in Hurricance country. I have the ethical issue well in hand, but I am starting to think about the client retention issue.
To elaborate: The typical garage opeing is 10' tall by 18' wide and assume that the header is the top of the bent. The wing walls are 2' wide braced panels that rest on a 8" wide unreinforced masonry wall of the same length, these are the side verticals of the bent. The lateral force applied to the top corner of the bent is around 10,000#. The way I calculate it, the moment at the bottom of the braced panel must be transmitted to the footing, through the foundation wall with reinforcing bars, not just J-bolts in the masonry alone.
Thanks for any help or insight you may offer.