Locker rooms usually exhaust directly outside (no return to the a/c unit) so you should not be condensing any of the humidity to have a latent load. ASHRAE table 7 of chapter 6 of the 2007 HVAC Applications recommends .5 cfm/ft2 for a ventilation rate. The latent load would depend on your makeup air for this exhaust rate. My Cooks "Engineering Cookbook" recommends an air change in locker rooms every 2-5 minutes.