Boiler1
Mechanical
- Jun 3, 2004
- 40
Dear gents,
I have unsuccessfully posted this topic few minutes ago so apology if a topic with the same subject shows up twice.
I would like to know if the latent heat load is always taken into account when sizing a cooling coil.
I am talking about situation where a cooling below dew point followed by the reheat is required in order to get the required relative humidity and dry bulb temperature.
Another question..
Why the typical system that does the above is usually set as: cooling below DP + reheat. Would it not be more economically viable to dehumidify first ( i.e. with desiccant wheel) and then to cool the air but this time ( as humidity ratio is lower ) the desired relative humidity will be reached before the dew point is hit.
This would eliminate the need for reheat coil and condensate pipework.
Does the desiccant wheel work with large air volumes ( 500-600 AcH/Hr)?
Many Thanks
I have unsuccessfully posted this topic few minutes ago so apology if a topic with the same subject shows up twice.
I would like to know if the latent heat load is always taken into account when sizing a cooling coil.
I am talking about situation where a cooling below dew point followed by the reheat is required in order to get the required relative humidity and dry bulb temperature.
Another question..
Why the typical system that does the above is usually set as: cooling below DP + reheat. Would it not be more economically viable to dehumidify first ( i.e. with desiccant wheel) and then to cool the air but this time ( as humidity ratio is lower ) the desired relative humidity will be reached before the dew point is hit.
This would eliminate the need for reheat coil and condensate pipework.
Does the desiccant wheel work with large air volumes ( 500-600 AcH/Hr)?
Many Thanks