L-Dowel Development Length

Status
Not open for further replies.

BadgerPE

Structural
Jan 27, 2010
500
Hey all,

Attached is a sketch of an arbitrary retaining wall. For the example a #5 dowel was assumed to be used and I am using ACI 318-08. My question is, because maximum tension occurs at the stem/footing interface, does ldh need to fall completely within the footing? Or is it acceptable for ldh to extend up into the stem? I would need about an 18" thick footing for this scenario which doesn't seem too bad, but if #8 dowels were used a 26" thick footing would be needed.

Thanks in advance!
 
Replies continue below

Recommended for you

You are transferring force of the stem into the base. It is no different than if you had a cantilever slab at a beam face. You need to develop the bar before it gets to the interface.

 