- Feb 10, 2009
- 85
Here we go again with another KVA vs KW problem!
As a UPS engineer, I was always told that the output rating of most UPS systems is given at 0.8pf. I obviously would always check the specifications but in general it is between 0.8 an 0.9 for the industrial systems that I work on.
When testing these systems with a purely resistive load bank I was taught way back in the day to only load test at 80% of the KVA rating to allow for the 0.8pf. I blindly followed what I was taught.
Now, as I get older (too quickly!), I question almost everything I do!
I have a 15KVA UPS (rated at 0.9pf), 115Vac out the specification says that the rated output current is 130AAC. If the rated output current is 130AAC then I would think that I should test this system at 130AAC for a full 100% load test. This is obviously 15KVA at approximately 1.0pf which is 15KW.
According to the way that I have been taught, I should test this at 117AAC (15KVA x 0.9pf / 115V).
Have I been taught incorrectly?
UPS engineer
As a UPS engineer, I was always told that the output rating of most UPS systems is given at 0.8pf. I obviously would always check the specifications but in general it is between 0.8 an 0.9 for the industrial systems that I work on.
When testing these systems with a purely resistive load bank I was taught way back in the day to only load test at 80% of the KVA rating to allow for the 0.8pf. I blindly followed what I was taught.
Now, as I get older (too quickly!), I question almost everything I do!
I have a 15KVA UPS (rated at 0.9pf), 115Vac out the specification says that the rated output current is 130AAC. If the rated output current is 130AAC then I would think that I should test this system at 130AAC for a full 100% load test. This is obviously 15KVA at approximately 1.0pf which is 15KW.
According to the way that I have been taught, I should test this at 117AAC (15KVA x 0.9pf / 115V).
Have I been taught incorrectly?
UPS engineer