oengineer
Structural
- Apr 25, 2011
- 732
I have an RFI that I need some help on. Here is the RFI:
"Contractor has identified an issue where the Gym joists that rest on the wall along gridline 12 have an incorrect chord extension due to an error by the joist manufacturer. As fabricated these joists' top chords only extend 2'-11 3/4" from the outside face of the wall, wheras they should extend 3'-4 7/8". They are correcting the issue and designing for joist extensions but need the following questions answered to do this:Can you provide us the actual DL and LL that the joist extensions need to be designed for? I am having trouble getting a section to work using the 1000 plf load that is shown on the main span."
Here is the plan view:
"Contractor has identified an issue where the Gym joists that rest on the wall along gridline 12 have an incorrect chord extension due to an error by the joist manufacturer. As fabricated these joists' top chords only extend 2'-11 3/4" from the outside face of the wall, wheras they should extend 3'-4 7/8". They are correcting the issue and designing for joist extensions but need the following questions answered to do this:Can you provide us the actual DL and LL that the joist extensions need to be designed for? I am having trouble getting a section to work using the 1000 plf load that is shown on the main span."
Here is the plan view: