AJ2002,
I think there may be a semantics issue here. I have reviewed some internal diagrams I have and IEC standards use a NC contact element off of an Over Load Relay in the control circuit diagrams as well.
I think where you may be getting confused is in the power circuit. IEC systems often use Motor Starter Protectors that are, for lack of a better term, what we in NEMA world would consider a "Manual Motor Starter". It includes the magnetic and thermal OL trip elements, as well as the disconnect mechanism. So because it has the disconnect, it is always shown in the Open position in the power diagram, as disconnects are shown in NEMA systems as well. But the difference is, if you had a control circuit auxiliary contact on one of these IEC MSP devices instead of a traditional OL relay, it will show as a NO contact, because the integral disconnect is Open.
Because JIC ceased to exist before the widespread use of these devices, there is no direct reference standard for showing them that I know of. Technically, because you need to show the MSP as an Open device (normal, de-energized), any aux. contacts associated with them will need to be shown as NO devices as well. What I used to do was to show them as NO, then add a label that said "N.O., Held Closed".
But if you are using a standard OL Relay that is controlling a contactor coil, the aux. contacts will ne shown as NC in a control logic diagram.