See the attached sketch. We’ve a 12.47kV feeder coming into a switchgear from the Utility. The Utility’s feeder has an ampacity of about 2500 Amps. It feeds into a single 12.47kV double ended switchgear through a main breaker. There are three more switchgears exactly alike this one that can tie into this switchgear through tie breakers.
The 12.47 kV switchgear is rated for 2000 Amps. We’ve discovered that all of the LT pickup settings of the main breakers are set at 1200 Amps, for all 4 switchgears – well below the bus rating, and less than one half the rating of the incoming feeders.
This was done by a very experienced company many years ago and it’s not nuisance tripped ever. Is there an underlying strategy for setting this main breaker up like that ? What would be any detrimental effects of bumping it up to 2000A to match the bus rating?