Is stranded wire inferior to solid core wire in this situation?

MiniMe4Eng

Electrical
Joined
Jun 19, 2015
Messages
130
Location
CA
I have to run 2x20A and 1x15A circuits on the outside of the house for like 9m (27') -that is RW90 in conduit.

I have been trying without success to find solid core wire (individual wires) cut by meter. I would have to buy a 300m spool. Even if I use the same color for all the wires and use tape to mark the ground/neutral and hot I am still under 100m.

From what I am seeing it would be maybe easier to get stranded core.
My plan is to get with exterior rated cable to inside of the house and there to connect using a junction box with NMD cables which will be easier to push pull through the finished ceiling (there is insulation there)

From what the vendors told me this wire is more popular because it is easier to pull but from what I am reading technically it is less performant.

Are there any major problems that I should be aware of when using stranded wire ?
 
Corrosion would be the most likely problem and slightly more likely to have problems at terminations unless ferrules are used.

Any moisture that enters the wire at the ends or small punctures will wick, carrying any corrosives with it.

Stranded wire was used between the anchors for the power at my house and the breaker panel - I would get water dripping into the panel as it ran down those strands during heavy rains.
 
Electricians almost exclusively use stranded for conduit pulls. Can't be many downsides to it that aren't relatively easy to overcome.
 
I am sure that many electricians do whatever is most convenient for them. No need to "overcome" anything if it's building in future repair work.
 
Pulling 15 or 20 A for house wiring means using either AWG #10 or AWG #8, depending on the "safety" factor.
For both of these sizes (in North America), the commercially available standard is a 7-strand construction, not single strand.
This could be why you are being stuck with a "minimum purchase" amount when opting for single strand conductor.

You should be able to find the stranded version direct off the roll - at whatever length you need - at the local hardware store or electrical supply store.
 
Stranded wire is preferred for every application except homebuilding where cheap is a condition of primary importance.

Stranded wire does not work as well in push in type connections. Those should be avoided regardless of wire type used.
 
They use it because they don't care if it fails sometime in the future. Good grief.

Isn't Romex type wire solid? Doesn't that get pulled in conduit? If individual wires are wanted there are jacket strippers and it is available in short lengths.

What was the original question - Is stranded wire inferior to solid core wire in this situation?

Is stranded wire the superior option with no drawbacks?
 
Electricians almost exclusively use stranded for conduit pulls. Can't be many downsides to it that aren't relatively easy to overcome.
That may be because building wires in AWG #8 and larger are not available in solid construction.
I have been retired for some time now, and things change but:
For over 60 years on the construction side, the standard was;
AWG 14, and AWG 12, solid wire.
AWG 10, solid or stranded.
All larger sizes stranded.
UNTIL THE INTRODUCTION OF THHN.
THHN became popular for conduit work, not because of the stranding, but because of the slippery and compact nature of the insulation.
Pulling 15 or 20 A for house wiring means using either AWG #10 or AWG #8, depending on the "safety" factor.
????
I started working as a helper, wiring houses on weekends while I was still in school, in 1956.
Some of the work was re-wires of houses built and wired in the '20s. 30's and 40's.
"either AWG #10 or AWG #8"
I seem to have missed that one.
Copper AWG #14 or AWG #12.
Aluminum AWG #12 or AWG #10
Have electricians wired millions of houses over the last 100 years and been doing it wrong?
Wait;
Have I made a mistake?
Am I not on Eng-Tips but on FaceBook by mistake?
#8 AWG is OK on FaceBook.
 
I apologize, Bill.
I am so used to rating ampacities for high temp environments I automatically derate everything ... you are correct. AWG 12 and 10 are FAR more common in residential construction at these current levels ...
 
I need to run:
-1x15A for hair dryer
-1x15A for smart toilet
-1x15A for an adjacent room (kitchen, the current circuit is tripping any time I have the hair dryer and a kettle on or kettle and a small convection oven)
-1x15A for lights (this is optional)

I need to run 27' in a PVC conduit (1") on the exterior of the house and then I can either switch to regular cable or continue with the same
I also have QBR15A that will go into a commander bc40200r1 panel (200A)

Here is chatgpt's solution for this

✅ Overview of Your Setup​

CircuitLoad TypeBreakerApprox. LoadLength
Hair dryer15A circuitQBR15A~12.5 A27' exterior + 24' interior
Smart toilet15A circuitQBR15A~8–9 ASame
Kitchen branch (oven/kettle)15A circuitQBR15A~13–14 ASame
Lights (optional)15A circuitQBR15ALow (<5 A)Same
  • All 15 A circuits
  • 3 or 4 circuits total
  • Exterior run = 27′ in 1″ PVC conduit
  • Want to use stranded RW90
  • One common ground
  • Panel: Commander BC40200R1 with QBR15 breakers

🔧 Step-by-Step Wire Sizing​

1. Conductor Type

  • RW90 stranded copper, 90 °C rated, outdoor-suitable
  • CSA-approved for wet/outdoor use when in conduit

2. Conduit Fill & Derating

ScenarioCCCs (Hot + Neutral)Derating (%)Resulting Ampacity (14 AWG RW90)
3 circuits6 CCCs80%25 A × 0.80 = 20 A ✅ OK
4 circuits8 CCCs70%25 A × 0.70 = 17.5 A ✅ OK
14 AWG RW90 is sufficient for all 15 A circuits, even if you include the optional lighting circuit.

3. Ground Wire Size

  • Shared #14 AWG copper RW90 is sufficient for up to 15 A per circuit
  • Must be green or re-identified with green tape

4. Conduit Fill (1″ PVC Schedule 40)

  • 14 AWG RW90 stranded4.8 mm²
  • 9 conductors (8 CCC + 1 ground) = 43.2 mm²
  • 1″ PVC allows 40% fill = ~215 mm²
✔️ You're well within the fill limit

5. Voltage Drop Check (27′ exterior + 24′ interior = 51′ total)

  • For 15 A on #14 copper: voltage drop ≈ 2.6%
  • Well below the 5% typical limit → ✅ No upsizing needed

✅ Final Wire List (If You Include 4 Circuits)​

Wire TypeQtyUseColor
#14 RW90 Cu4Hot wiresBlack, Red, Blue, Yellow (or mark with tape)
#14 RW90 Cu4NeutralsWhite (mark with tape to match circuit)
#14 RW90 Cu1Ground (shared)Green or green tape
→ Total: 9 conductors in 1″ PVC conduit = ✅ code compliant
If you drop the lights circuit:
  • Only 6 CCCs → better derating (80%), easier pulling

🔌 Breaker Compatibility​

Your QBR15 breakers in the Commander BC40200R1 panel are:
  • Bolt-on
  • Rated for solid copper
  • Do not accept stranded wire directly

✅ Solution:​

  • Splice stranded to solid pigtail in a junction box near the panel (fully code-compliant, as discussed earlier)

✅ Summary​

ElementRecommendation
Conductor type#14 AWG RW90 stranded copper
Ground wire#14 AWG RW90, 1 shared, green
Circuits allowed4 (15 A) in 1″ PVC with full compliance
Breaker typeQBR15 — use solid copper pigtails
Voltage dropAcceptable (≤ 3% over 51′)
Junction boxesRequired at transition to solid pigtail

 
The problem is: where do I find solid pig tails :-))

I suspect this can be done with regular cable, not RW90
 
From what I am reading I have the option to buy a spool of 300M of white and mark it with colored tape
 