jcfoley
Mechanical
- Feb 18, 2005
- 90
As you gentlemen have been so much help in the past, I wonder if you would mind verifying my assessment regarding an IS device installation.
Basically, a 4-20 mA transmitter is connected to a zener barrier and then to a PLC. The transmitter has no hazardous ratings whatsoever. An IS circuit is protected not only by a power limiting barrier but also by preventing a device (or even the wiring) from storing enough energy to create a spark. If the device has never been investigated or approved for this function (via the entity parameters) then the complete circuit is not an IS circuit. Right?
Now considering that I have a Class I, Div 2 location, would a non-hazardous transmitter used with a barrier be considered non-incendive?
Thanks
Basically, a 4-20 mA transmitter is connected to a zener barrier and then to a PLC. The transmitter has no hazardous ratings whatsoever. An IS circuit is protected not only by a power limiting barrier but also by preventing a device (or even the wiring) from storing enough energy to create a spark. If the device has never been investigated or approved for this function (via the entity parameters) then the complete circuit is not an IS circuit. Right?
Now considering that I have a Class I, Div 2 location, would a non-hazardous transmitter used with a barrier be considered non-incendive?
Thanks