Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Is an Equipment Ground Conductor required for Instrument Control Conduits

Status
Not open for further replies.

Grateful_A

Electrical
Joined
May 18, 2019
Messages
1
Location
US
Hello, curious what ya'll think.

The engineer on a project I am building is not requiring an equipment ground conductor to be installed with the control conduit for 4-20 mA twisted shielded pair cable to from the PLC to instruments. We'll tie the cable shield to ground at the PLC, but we will not have a separate equipment ground to ground the metallic conduit at either side of the run. This would honestly be the first time that I have not run an equipment ground in a control conduit to ground the conduit at each end to the enclosure/instrument.

Any thoughts on the removal of the equipment ground conductor in this particularly installation?
 
Maybe the drawings are showing comply with NEC bonding/grounding practices as a general note?
Is not the grounding/bonding of conduit/equipment cases/enclosure a code rule?
 
An equipment grounding conductor for 4-20 ma equipment is general practice in many industries and in many engineering standards.
However the Canadian Electrical Code does not generally require equipment grounding for class 1 and class 2 circuits.
The NEC is often very similar to the CEC.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top