IRC Braced Wall Design - holddowns?

Status
Not open for further replies.

Ben29

Structural
Aug 7, 2014
332
I am using the CS-WSP method set forth in chapter 6 of 2018 IRC. Am I to understand that you do not need a hold-down device (ala Simpson Strong Tie) as long as you don't take the 0.8 Adjustment factor (Item #5 in Table R602.10.3(2))?

I am following the Fastening Schedule per Table 602.3(1) and all other requirements relative to minimum wall length, wall location relative to corners, etc.
 
Replies continue below

Recommended for you

The 800 lb hold-down device in that table is only for WSP, not CS-WSP.

Take a look at the end condition requirements. There are some cases where a hold down is required. R602.10.7
 