Suggestion to sparks22222 (Electrical) Aug 2, 2002 marked ///\\Thanks guys for the replies, sorry i was a bit vague with the question.
anyway, there is an input and output chokes before and after the inverter so its well protected from overvoltage.
///These chokes are essentially for harmonic mitigation, that may eventually produce some overvoltages. However, the normal protection for overvoltages or spikes is a Transient Voltage Suppressor.\\Everthing was properly checked and earthing is ok.
We are not sure of lightning yet, but we have decided to use a power monitor on the incoming supply to monitor and download the voltage from the generator, in case there is any overvoltage coming from this generator.
///If you are in an area with lightnings, the proper lightning protection is recommended, e.g. air terminals according to NFPA 780.\\No fuses are blowing.
All that happened was the inverter failed and there was no display even on the inverter.
its just a coincedence that two electronic cards have failed in six months on a one year old plant from a generator supply.
We have a seperate electric supply we use at night for tank heating which is not big to run the whole plant but maybe enough to change to this supply for the inverter to prevent any overvoltage.
any more suggestions please pass them on.
///There also may be Electromagnetic Interference (EMI). EMI measurements are suggested.\\thanks