The interstital floors contain duct and piping. No equipment is allowed. The interstitial floors are unoccupied space, unlike mechanical or equipment rooms, and have separate designation for lighting requirements by IESNA, are their own smoke control zones separate from mechanical/equipemt rooms, do not require sprinkler coverage as would typcially be required fo mechanical/equipment rooms, and are recognized as different space than MER's by the 1998 ASHRAE HVAC Design Manual for Hospitals and Clinics. Having worked in multiple locations, hospital and laboratory, the current location is the first time I have seen ventilation air included. The interstitials have a 2-hour separation from occupied floors above and below, and 1-hour separation from mechanical rooms.
IMC 406.1 specifically includes ventilation air requirements for unoccupied space. ASHRAE 62.1 does not have a standard for unoccupied space, though the 0.06*SF would probably be closest category. Generally, they are interior zones, and need cooiling/dehumidication only, as on a cool day like today (36*F) you need to take off your coat to chase out duct or pipe runs.
I'm in favor of ventilatio air even if not mandated, as purge will be needed whenever renovation is performed to change occupancies in above or below occiped areas, and the interstitial floors include large amounts of asbestos containing material. Construction was done before ASHRAE 15 publication and includes refrigerant lines. That would probably dictate purge air, but not ventilation air.