I'm seeking your opinions about whether an exception for lateral loads in the IEBC (International Existing Building Code) can be applied to structures that are NOT buildings. I have just purchased access to this document, so I'm just beginning to look for answers. This question pertains to an industrial 140 foot tall heater structure, (half of that height is exhaust stack), whose foundation footprint is 36' x 20'. The client wishes to increase the height of the convection section, which increases the overall height. Wind shear is increased about 9%.
The exception to 2015 IEBC section 1103.3 says "the lateral force-resisting system of EXISTING BUILDINGS to which additions are made shall comply with sections 1103.3.1, 3.2, 3.3. Exception #2: Any existing lateral load-carrying structural element whose demand-capacity ratio with the addition considered is not more than 10 percent greater than its demand-capacity ratio with the addition ignored shall be permitted to remain unaltered."
My analysis concludes that the addition causes the allowable soil bearing capacity to be exceeded by 6%. Would it be appropriate to include in the report of my findings that the foundation is adequate because of the IEBC exception?