Oct 21, 2010 #1 Leinster Mechanical Joined Sep 14, 2010 Messages 36 Location KE Why is it necessary to have such large peripheral vents and a central vent on an Internal Floating Roof as per API 650. Surely if you satisfy the venting requirements as per API 2000 that should suffice?
Why is it necessary to have such large peripheral vents and a central vent on an Internal Floating Roof as per API 650. Surely if you satisfy the venting requirements as per API 2000 that should suffice?
Oct 21, 2010 #2 IFRs Petroleum Joined Nov 22, 2002 Messages 4,680 Location US The vents are for circulation, to dilute the small amount of vapors that get past the floating roof until they are below the LEL. Upvote 0 Downvote
The vents are for circulation, to dilute the small amount of vapors that get past the floating roof until they are below the LEL.