Intermediate Precast Structural Walls

Status
Not open for further replies.

palves

Structural
Joined
Jun 6, 2008
Messages
61
Location
US
I'm working on an existing building and trying to justify that the tilt-up walls can be classified as "Intermediate Precast Structural Walls". It looks like the main difference between "ordinary" and "intermediate" is Section 21.4 in ACI318-08. My problem is that I don't understand exactly that section wants me to do. My detail to tie the panels together consists of a steel plate that uses post-installed epoxy-grouted threaded rods into each panel. Based on Section 21.4 I have to determine whether or not my connection is yielding and then develop 1.5*Sy if it isn't. All of that seems to refer to rebar that is cast into the panel, but I used Appendix D to size my connection. Is Appendix D sufficient or do I still need to develop 1.5*Sy? Any ideas out there?
 