The magnet wire insulation has a higher voltage rating. In the past, motor winding insulation was supposed to be 2x the line RMS rating. So a 480V motor would have 1000V insulation. In some cases motor mfrs in North America would just use 1200V insulation so that they didn’t need to use different magnet wire for 460 or 575V motors. But inverters can cause standing waves that reflect back and forth between drive and motor, building up as it does until it can easily exceed 1200V. So NEMA and IEEE came up with a design standard calling for inverter rated motors to use 1488V as the MINIMUM design standard for magnet wire. But subsequent investigations have found that under certain conditions, the spikes can reach up to 3x the DC bus voltage, so on a 480V drive that is 2150V. So many wire suppliers exceed that minimum spec, the result being that 2200V has become very common and I have seen some up to 3000V.