Read my post, Mr. Che.
The test circuit is as follows:
Test instrument to ground loop.
Ground loop to earth.
Earth to electrode under test.
Electrode under test to test instrument.
The connection is a series connection.
The conductor to the electrode under test may be broken and an Ohmmeter inserted or a ground loop tester may be used without breaking the conductor.
Stakeless Ground Loop Tester.
Stakeless earth ground loop testing
June 12th, 2017, Published in Articles: Vector
Testing the grounding components of equipment in hard-to-reach spaces is challenging. Fluke, represented locally by Comtest, now has the Fluke 1630-2 FC stakeless earth ground clamp, a heavy-duty clamp jaw that stays in alignment and in calibration even in industrial environments. Staying online to identify ground loop resistance without the need to disconnect, then reconnect the earth electrode from the system, is now possible. This clamp measures earth ground loop resistances for multi-grounded systems using the dual-clamp jaw. This test technique eliminates disconnection of parallel grounds, as well as finding suitable locations for auxiliary test stakes. The 1630-2 FC supports the Fluke Connect wireless system, which connects the clamp wirelessly with an app on a smartphone or tablet.
Link
A stakeless test requires at least two ground electrodes and measures the sum of the two resistances to ground.
Preferably there is a ground grid or array of ground electrodes.
The stakeless test always returns the sum of the resistances of the electrode under test and the ground grid or array.
The resistance of the electrode under test will always be less than the total resistance indicated by the test meter.
Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!