We have a 460VAC 3 Phase DC power supply in a design that has internal fuses protecting the line inputs. We have a 20A D characteristic breaker on the incoming power. Additionally, we have 3A fuses external to the power supply. The installation instructions for the supply state the following:
"The unit is protected with internal fuse (not replaceable) at L pin and it has been tested and approved on 20A (UL) and 16A (IEC) branch circuits without additional protection device. An external protection device is only required if the supplying branch has an ampacity greater than above. Thus, if an external protective device is necessary, or, utilized, a minimum value of 13A B- or 6A C- characteristic breaker should be used."
Are the fuses necessary? If not, can we get rid of the fuses if we use a different breaker?
"The unit is protected with internal fuse (not replaceable) at L pin and it has been tested and approved on 20A (UL) and 16A (IEC) branch circuits without additional protection device. An external protection device is only required if the supplying branch has an ampacity greater than above. Thus, if an external protective device is necessary, or, utilized, a minimum value of 13A B- or 6A C- characteristic breaker should be used."