We are building a new plant in which we are using smart MCC's throughout the plant. Each starter in the smart MCC contains an Allen Bradley E3+ solid state overload relay.
All of the starter buckets are for 480V motors and use 120V AC for the field and internal bucket controls.
We recently have been seeing a number of cases where we have been getting some kind of induced voltage (most likely capacitively coupled)on our control wires giving us false inputs to the solid state relay. This induced voltage is in the range of about 18-28V and is just on the border of the turn on voltage of 20V required for the inputs to the solid state relay. These occasional false inputs are causing problems with the operation of these starters and their control.
After doing some testing I found that the open circuit voltge on these control wires when removed from the input on the relay is about 65V. I am trying to determine where this coupled voltage is coming from. All contors for each starter are supplied from a control transformer within the bucket so when bucket breaker is off, control power is off.
When I shut the power off to the bucket all of this induced voltage dissapears. This tells me that the induced voltage is a function of the wires origonating from this bucket and not from some other circuit elsewhere in the plant. I can even isolate it to when a particular wire in the control wire is removed the induced voltage drops significantly When looking further, I noticed that in the several cases where this has appeared, the contorl cable has been a multi-conductor cable.
Now I know long distances can be a major factor in this type of coupling, and that a typical solution is to use DC controls. However in the 8 or so cases that I have seen there have been some long and some short distances and they have been in different areas of the plant. I am able to bleed the induced voltge off and eliminate the false input by connecting a capacitor between the input and ground.
I am concerned that I will continue to see this problem. Although a capacitor has been a sort term solution, I do not want to have to go sticking capacitors in every single starter. Has anyone ever seen this on happen this abundantly thoughout a plant? Are solid state relay devices specifically suseptiable to this kind of voltage? Am I missing something or maybe overlooking something that could be a source of the problem?
All of the starter buckets are for 480V motors and use 120V AC for the field and internal bucket controls.
We recently have been seeing a number of cases where we have been getting some kind of induced voltage (most likely capacitively coupled)on our control wires giving us false inputs to the solid state relay. This induced voltage is in the range of about 18-28V and is just on the border of the turn on voltage of 20V required for the inputs to the solid state relay. These occasional false inputs are causing problems with the operation of these starters and their control.
After doing some testing I found that the open circuit voltge on these control wires when removed from the input on the relay is about 65V. I am trying to determine where this coupled voltage is coming from. All contors for each starter are supplied from a control transformer within the bucket so when bucket breaker is off, control power is off.
When I shut the power off to the bucket all of this induced voltage dissapears. This tells me that the induced voltage is a function of the wires origonating from this bucket and not from some other circuit elsewhere in the plant. I can even isolate it to when a particular wire in the control wire is removed the induced voltage drops significantly When looking further, I noticed that in the several cases where this has appeared, the contorl cable has been a multi-conductor cable.
Now I know long distances can be a major factor in this type of coupling, and that a typical solution is to use DC controls. However in the 8 or so cases that I have seen there have been some long and some short distances and they have been in different areas of the plant. I am able to bleed the induced voltge off and eliminate the false input by connecting a capacitor between the input and ground.
I am concerned that I will continue to see this problem. Although a capacitor has been a sort term solution, I do not want to have to go sticking capacitors in every single starter. Has anyone ever seen this on happen this abundantly thoughout a plant? Are solid state relay devices specifically suseptiable to this kind of voltage? Am I missing something or maybe overlooking something that could be a source of the problem?