Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Indoor Vs Outdoor Termination kits 2

Status
Not open for further replies.

NickParker

Electrical
Joined
Sep 1, 2017
Messages
455
Location
NL
Termination_kit_indoor_outdoor_uiy7pv.jpg


Why the termination kits are applied only for medium voltage and above?
Why skirts are used in outdoor termination kits?
 
Skirts are used to increase tracking distance.
Termination kits typically feature either stress cones or an alternate method to reduce voltage gradient stress at the end of the cable insulation.
Before kits were introduced, stress cones were field fabricated by trained "Cable splicers."
Smaller contractors would have to "Sub out" the termination of medium and higher voltage cables.
The introduction of termination kits allowed industrial electricians to complete the cable terminations.

--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top