jayrod12 -
What testing field procedures can you field for field testing and sampling of mortar? ASTM C270 controlled mortar designs and properties.
The ASTM C270 specification clearly states that it is not a specification to determine the mortar strength.(Section 3.1 relating to Specification Limitatations).
There are two different methods to determine the type of mortar: proportions specifications or properties specifications and two cannot be interchangeably - just one or the other. The property specifications are used to determine proportions a material proposed to be used when mixed to controlled flow, which is does not produce a workable mortar that is desired for a quality wall.
The two tables in C270 (Table 1 and Table 2) are used differently. It clearly states that the compressive strength applies only to laboratory prepared samples and not to field samples.
If you look at Table 2, you will see very little difference in the properties except air content for different cementitious materials and it just a table to define the mortar type from the broad range of a gray scale.
It is definitely not like a simple ready-mix design where the only real site tests are for compression strength (field prepared sample is non-absorbant mold cured under laboratory conditions) to provide and idealistic measure of the in-place concrete and the site-meaningful measures of the air content of the mix itself and the slump, which is a measure of the ability to be placed for the application.
Table 1 is a more practical table because it proportions of the materials to determine the proportions of the approved materials to be used. Again, looking at the table, you see there is a broad range of proportions to the used for different mortar types.
The observation on the in place strength of the mortar strength is very obvious, especially because it is used as a very thin layer between absorbent materials (masonry units)in compression compared to lab samples that are cubic (shear failure) prepared with non-absorbent materials.
Looking at individual materials (mortar, masonry units, grout) in a masonry wall is almost like determining the acceptable materials (cement coarse aggregate, fine aggregate) of concrete before it is placed in concrete forms. - It can be a little confusing to be precise when the site use really dictates the real performance of the structural element (wall or slab).
Dick
Engineer and international traveler interested in construction techniques, problems and proper design.