I have a couple of questions.
1. Is this a suspended structural slab or SOG?
2. How thick is the slab?
3. How old was the slab before cores were taken?
4. Have you noticed any drying shrinkage cracking in area placed prior to commencement of rain and also the area placed during rain?
5. Was the area that was placed prior to commencement of rain protected while it was raining?
6. Were cores also taken from the area which had been placed prior to rain?
7. In addition to the tests you have in mind, will any of the cores be tested for strength and subjected to some limited petrographic analysis?
Some ASTM Standards to consider are:
ASTM C42-Standard Test Method for Obtaining and Testing Drilled Cores and Sawed Beams of Concrete---note 5 in this standard recommends that the concrete be at least 14 days old prior to coring. ASTM C642-Standard Test Method for Density, Absorption, and Voids in Hardened Concrete, and some of the test methods in ASTM C856-Standard Practice for Petrographic Examination of Hardened Concrete to evaluate the microstructure of the sample.
For some more ideas, check this thread which was started by Ron