You have an air balance problem,Contractor should be held responsible for this situation. Each room requires a certain amount of CFM acording to the load. This should have been determined when the system was sized.Do this
1. Do a heat load calculation on this home
2, This will determine the amount of CFM for each room.
3, Measure static pressure step-by-step. First, read the nameplate data on the air handler or furnace to determine its static pressure rating. This is often the maximum amount of static pressure or resistance that the fan can handle and still deliver 400 cfm/ton on high speed.
Second, since total external static pressure is what we're measuring, we'll need to take two readings: one on the supply side of the fan, and one on the return side of the fan.
To measure in-duct air pressures, drill two 3Ú8-in. holes in the duct to insert the static pressure tip.
Third, connect the static pressure tip to the hose, and attach the hose to the pressure connection on the Magnehelic® gauge. The top (or high connection) is for positive or supply pressure. The bottom (or low connection) is for the negative or return pressure.
Fourth, level and zero the pressure gauge to ensure accurate repeatable readings. Then insert the static pressure tip into the duct with the tip facing into the airflow.
Fifth, read the pressure on the gauge, and record the reading on the supply side, then on the return side. These readings can be taken at one time, but diagnostic ability increases when each side is read separately.
Use a (+) sign before the positive or supply side reading to show where it was taken, and a (-) sign before the negative or return side reading.
Add the two pressures. Disregard the positive and negative signs before the pressures, because each pressure is an absolute number &emdash; each pressure is "seen" and affects the fan as a force, so they must be added together to determine the total resistance the fan sees. For example a +.23 w.c. plus a -.19 w.c. equals a total static pressure reading of .42-in. w.c..
Record the pressure readings on your diagnostic report or on your service ticket. Our techs often write the pressures on the cooling coil for future use. Any change in static pressure reveals a change in the system that should be addressed for the system to operate properly.
Most residential and light commercial systems under five tons are rated to deliver 400 cfm at a static pressure of .5-in. w.c. Maximum static pressure increases with larger units.
Be certain to always read the nameplate data to determine the total static pressure that the unit was manufactured for. Also, obtaining a copy of the manufacturer's fan curve data can be very helpful in interpreting static pressure and airflow readings. Hope this helps