Was away from the simulation software all weekend.
Can't provide a truly simple one-line; just imagine a geographic region that has 12-15 lines in one "path" presently, 2/3 of which are 500kV, the rest lower voltages, none of which are compensated. Then throw a pair of 70% compensated 500kV lines into the path, as well as all the other interconnecting lines, and I don't know how much of it can be "simplified" without changing the results.
With full compensation I see fault currents about 180 out of phase from when there is no compensation, or the compensation is very small. I need to do some more investigation and will report back if I find something interesting.