dinkelja: I think you must be using USA terminology and talking about the distance from a motor control center (MCC) to the motors. If you are talking about IGBTs, the motors must be connected to variable frequency drives (VFDs) in or near the MCC.
With IGBT switching in VFDs, there is a transmission line voltage reflection effect that creates high voltage spikes from the square voltage pulses. There is a critical cable length that plays a role in that effect. Anything more than 25 feet is likely to be a problem. If you can put the VFDs really close to the motors, the voltage spikes might be eliminated.
For withstanding voltage spikes and for other reasons, it is also important to use only motors that are rated and nameplated for use with VFDs. There are also VFD output filter units (output reactors) that are designed to reduce voltage spikes. With VFD duty motors, perhaps with filters, the motor cable length won't matter so much.