For VFD novices, screw compressors are a tricky application with VFDs. I agree with Gunnar but take it a step further. Often times people replace starters with VFDs on screw compressors and just use the VFD like a starter without reconsidering what the system is CAPABLE of now. The cut-in pressure is now something that is less important, because you CAN just reduce the speed instead to match the pressure demand, thus reducing the number of times the motor must start and stop altogether. But by just replacing the starter with a VFD and using it in the same way, EVERY time the VFD has to start the motor, you are thermally stressing the transistors as they accelerate it. Running it for longer periods allows them to cool off, but under heavy use, the pressure switch drops out and restarts it again too soon. The thing that you need however is a pressure TRANSDUCER giving an analog value to a PID loop in the VFD instead of just a pressure SWITCH, and someone that understands how to make that work in your system.